Browse Forums Home Theatre & Automation Re: 240V cable and HDMI/HDMI over CAT6 together in conduit O 2Mar 15, 2011 11:50 pm Kodiak Data Cabling onFaceBook Consult*, Design and Installation Data, TV, Home Theatre/ AV Cabling, Multi Room Audio, IP CCTV and Door Intercoms Ask for a Quote. *DIY DATA Cabling Is Ilegal Re: 240V cable and HDMI/HDMI over CAT6 together in conduit O 4Mar 16, 2011 4:13 pm Kodiak Data Cabling onFaceBook Consult*, Design and Installation Data, TV, Home Theatre/ AV Cabling, Multi Room Audio, IP CCTV and Door Intercoms Ask for a Quote. *DIY DATA Cabling Is Ilegal Re: 240V cable and HDMI/HDMI over CAT6 together in conduit O 8Mar 17, 2011 7:45 pm Kodiak Data Cabling onFaceBook Consult*, Design and Installation Data, TV, Home Theatre/ AV Cabling, Multi Room Audio, IP CCTV and Door Intercoms Ask for a Quote. *DIY DATA Cabling Is Ilegal Re: 240V cable and HDMI/HDMI over CAT6 together in conduit O 11Mar 17, 2011 9:32 pm E1109 Best reference for this is AS 3000:2007 clause 7.5 in regards to separation from low and extra-low voltage wiring. Can't find this doc online/looks like a "paid for doc" (which I find strange). Can you confirm what is the min separation distance - would be nice for my own reference simply to check that the electrician and cabler aren't running next to each other when I do get to checking out the wiring. Re: 240V cable and HDMI/HDMI over CAT6 together in conduit O 12Mar 18, 2011 5:22 pm jklow888 E1109 Best reference for this is AS 3000:2007 clause 7.5 in regards to separation from low and extra-low voltage wiring. Can't find this doc online/looks like a "paid for doc" (which I find strange). Can you confirm what is the min separation distance - would be nice for my own reference simply to check that the electrician and cabler aren't running next to each other when I do get to checking out the wiring. Yep, you have to pay to download it from the SAI Global website. I'll check at work tomorrow for you, its beer o'clock here in Darwin Re: 240V cable and HDMI/HDMI over CAT6 together in conduit O 13Mar 18, 2011 9:38 pm Hi, There is some information about separation in the AS/ACIF S009 wiring rules on page 56, section 16.3. In summary, the services can be separated by
To answer your original question, you could run the 240V in the same conduit as the Cat6, but you would need to sub-duct the 240V inside another conduit (orange) inserted inside the white communications conduit (this in accordance with section 16.3.3 of S009), but it wouldn't make sense to go to this expense when you can just run the 240V cable on the other side of the joist Paul Re: 240V cable and HDMI/HDMI over CAT6 together in conduit O 14Mar 18, 2011 9:56 pm if you want them at the same spot then just use two conduits.. that is how they wire your phone line from the street, it sits side by side with the electrical conduit in most cases. the conduit would need to be undamaged regardless of what network is in play. The conduit needs to be able to have fibre run through it. NBN and Opticomm are just… 4 2893 If there have been changes, variations, during construction then the drawings should be revised, the building permit amended and the current, as built drawings given to… 2 4491 Hi everyone, Looking for some advise. We are about to build an above ground pool in our backyard. There is a private sewer line running under the pool at 1.6m… 0 11763 |