Browse Forums Building A New House 1 Oct 12, 2013 5:22 pm Hi all, We are currently building a 2 story house in Adelaide and wondering if anyone knows what the maximum overhang Hebel can be on a slab? our slab measurements are out. Currently the Hebel on our slab is hanging over on most parts of our facade 3.5cm - 4.5cm. Also on one section part of the slab juts out (20cm long) the Hebel falls short by 3cm, it looks really messy and stands out is it possibly to cut that part of the slab away? Re: Hebel overhang on slab 2Oct 27, 2013 7:15 am That should be a problem for your builder, I would think? Re: Hebel overhang on slab 3Oct 27, 2013 7:30 am BCA requires that ‘Exterior masonry must not overhang more that 15mm past the edge of the slab' Remedial measures are possible to solve this such as bolting an angle on below the Hebel. As far as the other issue is concerned it should be possible to cut the slab back The Harder You Try - the Luckier You Get ! Web site http://www.anewhouse.com.au Informative, Amusing, and Opinionated Blog - Over 600 posts on all aspects of building a new house. In the end, two pieces of treated timber (20mm thick) were bolted onto the joists and planed when there was too much sticking out. Passed inspection. 13 7800 Thanks Ardo, they are sort of semi concealed. I think it is only a few millimetres. I see if they can adjust the hinges. 4 3797 I was looking at different options for a fence for my build and Hebel PowerFence seemed like a good option (one of the criteria was a solid wall look). However, I don't… 0 5902 |