Browse Forums Heating, Cooling & Insulation Re: Ducted zone not working now 6Mar 25, 2022 1:02 pm vijaytee1 I have a 5 zone ducted air system in my house. Today zone 3 will not work (media room and study room). What would have caused it? Also say i set the temp to 22degress. Once the lcd reaches 22 degress my ducted cuts off. Why? Systems 6years old. Never had nothing wrong. I always clean the filter also. I have a carrier lcd plate and zonemaster ducted system 16kw. Does it come back on when the temperature increases or does it stay off? Re: Ducted zone not working now 8Mar 25, 2022 1:54 pm vijaytee1 It comes back on if i lower the temp. But no wont come back on once it hits the set temp on my lcd screen Some units can have additional settings that are commonly used in hotels and offices. One of these is a cutoff range. For example if you set it to 20c it will cool to 20c and shut off, then it wont turn back on until you reach say 25c or 30c and then it cools back down to 20c and shuts off again. And when you manually lower it from 20c to 19c it then kicks back on until it hits that set temp. It would be pretty unusual to have turned on in a residential setting, but it could be the case. Of course that won't be the case if yours is shutting off and not turning back on regardless of how hot it gets. I had a similar issue with my fridge not too long ago. It wasn't the same model, but the symptoms were pretty much the same: the compressor would start and then stop… 3 7536 Yes it had a house on it. But Melbourne water only wanted something the original size of the existing house. We managed to fit a 45sq house on. 10 33666 Hi All It has been a few weeks since my last update. The build has been progressing well. No major issues to report. The scaffolding was dropped today, gyprock will be… 96 356976 |