Post subject: Electric cable standard - 2.5 mm2 twin & earth cable enough?
Posted: Aug 29, 2011 9:41 pm
Junior Member
Joined: 23 Mar 2011 Posts: 32
Hi all
Building a house at the moment and just finished electrical wiring. When I inspected the house on last weekend, I noticed the electric cables for lighting and powerpoints are using 2.5 mm2 twin & earth cable (2.5mm2 x 2c+e).
Not sure whether this is sufficient to support all downlights and powperpoints (there are about total 45 downlights and 25 powerpoints through the house).
Also, should the kitchen applicance (e.g. canopy, oven, microoven, dishwasher and cooktop) using different size cable, say 4mm2 twin & earth cable? or 2.5mm2 twin & earth cable is enough?
What is the Australian standard for the electric cable that builder should use?
Post subject: Re: Electric cable standard - 2.5 mm2 twin & earth cable eno
Posted: Aug 30, 2011 10:56 pm
Loyal Member
Joined: 24 Oct 2010 Posts: 92 Location: Argyle WA
This isn't something you need to really worry about.
Electrical is the most highly regulated and inspected trade. Telling the difference between a 2.5mm and a 4mm can be difficult for someone who isn't in the trade.
Depending on the cable installation conditions 2.5mm2 can be sufficient for an oven, as long as it is installed correctly and the rating of the oven is taken into consideration, but most importantly the rating of the breaker will be matched to the cable.
Post subject: Re: Electric cable standard - 2.5 mm2 twin & earth cable eno
Posted: Sep 01, 2011 4:27 pm
Senior Member
Joined: 14 Jan 2010 Posts: 138 Location: Victoria
the other posters here are NOT electricians... read below.
there is NO magic cable size that is dictated to builders or electricians to be used for specific jobs. In fact a builder has nothing to do with anything electrical... other than deciding on where things are placed and adding 30% ontop of our rates cable sizes and circuits are all decided in planning stage by the electrician or electrical engineers. They are decided on a multitude of factors !! in fact there are 3 books with hundreds of pages that we need to know inside and out to determine cable sizes their effects, and effects on the cables themselves due to other factors. I wont go into details because it will sound like an overseas language... BUT heres a basic rundown, hopefully it will enlighten you to trust your electrician... he has done 4 years worth of schooling with MAANY regulation tests and MANY years in the field so you can have your lights switch on and power for your toaster.
you can have UNLIMITED powerpoints on a circuit of 2.5mm cable as per australian standards and regs.. the reason why they are split up is because of convienence when a fault occurs, i.e you dont want ALL of the house powerpoints turning off in the event of an appliance fault.. this too is mentioned in our regulations and standards. i.e. i run 10-15 gpos per circuit, others do 20-25, i know a sparky that does 5 per circuit!it all depends.
an oven feed in 80% of volume builder estate homes are wired in 2.5. this is because the ovens supplied dont warrant the need for a large cable type, there is also cable run lengths taken into consideration that MIGHT make the cable bigger to accomodate voltage drop.. but this is rare in an estate house.. so what dictates an oven cable size is: length of the run of cable, current draw of the oven, characteristics in which the cable is run, i.e. enviroment, thermal effects, insulation etc etc etc i wont go into details this is electrician talk , there is no ' standard ' one size fits all.
1.0mm and 1.5mm are the most common sized cable for light circuits , depending on the electrician/job. not every single light in the house is on the one run of cable. This too is split up to accomodate different load types, number of lights, fault convienence, fault loop impedeance etc etc etc..
also you question regarding the appliances... there are all ran in the same type of wire as the other powerpoints ( 2.5mm ).. again depending on how the electrician wired it, dictates how he/she has split their circuits up. there is no reason to run 4mm for general purpose outlets, ( and you wouldnt get 2 x 4mm cables into a powerpoint! ) this sized cable can supply up to 32amps ( give or take depending on cable runs, external effects etc ) mainly ran for LARGE air conditioners, swimming pool gear, VERY long runs of cable, induction cooktops, large double ovens, other specific equipment.
i hope this shed some light, basically all you need to worry about is do the lights turn on? is there power at the powerpoints? and i safe to use this equipment? dont fret over cable sizes.. your sparky will know exactly what they are doing
Post subject: Re: Electric cable standard - 2.5 mm2 twin & earth cable eno
Posted: Sep 03, 2011 10:16 pm
Senior Member
Joined: 26 Mar 2009 Posts: 127 Location: Lithgow NSW
ChargerWA wrote:
cenemelectrical wrote:
the other posters here are NOT electricians... read below.
My "A" Grade electrical license begs to differ.
What parts of Cene's post do you disagree with Charger? I am an Electrical trades also (although now drive a 500MW generator), and cant see any issues. I agree that unless people wish to read both AS3000 and AS3008 then they have no choice but to go with the guidance of the Electrician.
Unless you have been physically involved in the trade over the last five years you wont even be able to identify the TPS T&E. Old 2.5mm is about the same size as new 4mm, and new 2.5 is like old 1.5mm.
The best and worst of these forums is the amateur input. I always appreciate if an "expert" can put some creds at the bottom of the post. So thanks Cene .
Post subject: Re: Electric cable standard - 2.5 mm2 twin & earth cable eno
Posted: Sep 04, 2011 12:09 am
Loyal Member
Joined: 24 Oct 2010 Posts: 92 Location: Argyle WA
ozberg wrote:
ChargerWA wrote:
cenemelectrical wrote:
the other posters here are NOT electricians... read below.
My "A" Grade electrical license begs to differ.
What parts of Cene's post do you disagree with Charger? I am an Electrical trades also (although now drive a 500MW generator), and cant see any issues. I agree that unless people wish to read both AS3000 and AS3008 then they have no choice but to go with the guidance of the Electrician.
Unless you have been physically involved in the trade over the last five years you wont even be able to identify the TPS T&E. Old 2.5mm is about the same size as new 4mm, and new 2.5 is like old 1.5mm.
The best and worst of these forums is the amateur input. I always appreciate if an "expert" can put some creds at the bottom of the post. So thanks Cene .
I disagree with the part where he says the other posters are not electricians. I am a qualified electrical mechanic with a fitters endorsement and the electrical nominee for the electrical contracting company I manage. I have worked as an electrician all of my life.
If you read my post I said the exact same things he did, just without all of the hyperbole.
Post subject: Re: Electric cable standard - 2.5 mm2 twin & earth cable eno
Posted: Sep 04, 2011 5:54 am
Senior Member
Joined: 26 Mar 2009 Posts: 127 Location: Lithgow NSW
[ I disagree with the part where he says the other posters are not electricians. I am a qualified electrical mechanic with a fitters endorsement and the electrical nominee for the electrical contracting company I manage. I have worked as an electrician all of my life.
If you read my post I said the exact same things he did, just without all of the hyperbole.
Hows that for your amateur input?[/quote]
I think maybe you are being overly sensitive Charger. The point is that there is a lot of unqualified advice given on the forum - sometimes good, sometimes not. If you are thrashing around paint colours, facade detail, then all is good. Otherwise, unqualified information can confuse the issue.
Cene's post probably had the detail that the original poster desired
Post subject: Re: Electric cable standard - 2.5 mm2 twin & earth cable eno
Posted: Jan 03, 2012 12:27 am
Junior Member
Joined: 13 Mar 2011 Posts: 6
I found I had to get my sparky to go a size up on a few cables to 'future proof' myself and run a few extra circuits to/from the circuit board. Eg, Bigger oven down the track, Pool equipment needing more power, A/C needing more power, (ended up running 3 phase) Spa hot pumps in ensuite needing more power, Being able to weld in my garage down the track, (dedicated circuit) Induction cook top provision(some up to 42 Amp!) Oven dedicated 32Amp circuit Separate circuits in each side of kitchen (went through all the crap I have with sparky in kitchen appliances and what is posssible to be on at same time and too much)
Cable cheap to throw in before the plaster goes on. I put power points in locations so the cable runs ended up in pretty much every wall. Makes adding power points down the track easy. Food for thought.
Post subject: Re: Electric cable standard - 2.5 mm2 twin & earth cable eno
Posted: Jan 03, 2012 7:59 am
Gold Member
Joined: 19 Mar 2007 Posts: 4242 Location: Sydney
Hitchy wrote:
I found I had to get my sparky to go a size up on a few cables to 'future proof' myself and run a few extra circuits to/from the circuit board. Eg, Bigger oven down the track, Pool equipment needing more power, A/C needing more power, (ended up running 3 phase) Spa hot pumps in ensuite needing more power, Being able to weld in my garage down the track, (dedicated circuit) Induction cook top provision(some up to 42 Amp!) Oven dedicated 32Amp circuit Separate circuits in each side of kitchen (went through all the crap I have with sparky in kitchen appliances and what is posssible to be on at same time and too much)
Cable cheap to throw in before the plaster goes on. I put power points in locations so the cable runs ended up in pretty much every wall. Makes adding power points down the track easy. Food for thought.
And this is why you get the electrician to do the work, but you get involved in what is happening. So education is good.
_________________ Demolition August 2009, Construction Started September 2009, Completed December 2010