So what I take from that is that my 7 downpipes to be compliant will only drain by design to be compliant 37 sq m each. A shortfall for me of 2.3 sq m per downpipe so multiply that by 7 is 16.1 sq metres short fall for my roof drainage.
Have I got that right SaveH20?
Have I got that right SaveH20?
Yes...but the figures aren't exact because I didn't know the exact roof area...but the drainage will come up short because the figures will be close and the discrepancy is large.
The calculations factor the maximum roof area that can drain to each downpipe, it is not the average drained to each downpipe because downpipes invariably drain different size roof areas.
Your builder will (if willing) be able to tell you the roof space area and the roof catchment (factored) area.
If you return to fzxbeetle's opening post on this thread, you will see that he has posted his roof areas as given to him by his builder. Note that the builder (Henley) were wrong with their drainage calculations as per those figures because they basically didn't have a clue.
Cheers SaveH20, what this discussion does show besides the numerous builds with non compliant roof drainage is that it is a rather difficult task on behalf of the average punter to have any idea if their roof drainage is compliant. Even our so called experts are not getting it right by looks of things.
The VBA technical solution sheet 0.04 that I have linked below also discusses roof drainage compliance with an example. Note that the technical solution sheet is a re-vamp of a former Victorian Building Commission technical solution sheet but it is a poor attempt...some things like the roof slope factoring isn't properly addressed and they have even left a downpipe off the last house diagram on page 6! Good on 'em. I give it a 4/10.
http://www.vba.vic.gov.au/__data/assets ... mwater.pdf